• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Factory/dealer screwup

Status
Not open for further replies.

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
They often are not good enough to prevent motor damage if the motor is running when you lose a phase. This is especially true when the motor is operated at its service factor horsepower....a practice done by some air compressor manufacturers to permit them to use a small motor than they really should.

However some newer electronic overloads have phase loss built in. If they installed a separate phase loss relay, I can only assume that their overloads do not have that function.
With the old school heaters in the magnetic motor starters I never had a problem burning up a running motor losing a phase. Current would increase on the remaining two and trip out. I can't say that since adjustable overloads have become common. Too many people jacking up the overloads so it becomes the next shift's problem
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
With the old school heaters in the magnetic motor starters I never had a problem burning up a running motor losing a phase. Current would increase on the remaining two and trip out. I can't say that since adjustable overloads have become common. Too many people jacking up the overloads so it becomes the next shift's problem
Have seen that exact thing happen many times with that type of equipment.
 

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
I did have a pump station one time that blew a primary on the poco side. I think the big pump was 250 HP 4160 volt. It was running and generating a false/weak 3rd phase. They lost some smaller 480v 3 phase motors. I can see it helping in that situation
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
These are powered off the line voltage, haven’t seen any like these before. Usually the electronic ones are powered by the current flowing through them. Apparently this is an issue with this manufacturer, they knew exactly what happened.
Yeah, if the control power for the SSOL was tapped off of the line, and the line voltage doubled, that would cause a RUDE (Rapid Uncontrolled Disassembly Event).
 
Status
Not open for further replies.
Top