Hi all!
I always enjoy this forum and respect all the good people involved with it.
I learn something everytime I come here and today I suspect will be no different.
I failed an above ceiling today for not supporting the 2x4 lay-in fixtures as per 2005 NEC 410.16 (c).
I used framing screws to attach the fixtures to the grid ( like I always do)
the inspector tells me that attaching to the grid is only acceptable if they are screwed to a "main" grid runner. I have read over and over again that particlular art. in the code and can't see what he see's.
I never try to argue with inspectors, and just hung all the lights with grid wire to be done with it, but would really like to know If I have been in violation all these years.
Your thoughts / comments will be appreciatied!