A water ground is a SUPPLEMEMTAL ground connection,one #6 from one ground rod is all you need if you can prove the ground w a tester. And its only valid if the water line is buried in the ground 12 ft b4 it comes up within a certain distance from the service entrance. I do not agree w inspectors requiring water grounding along w ground rods and bonding pex water pipes at the metal clips at water heater,its not required and if it was your ONLY ground connection you would have to dig water line up to prove its validity as a ground source....its supplemental ,not required. We put 2 ground rods in because no one has a ground tester to prove that one is enough,to be failed b/c you included a water ground is crazy.