Hi everyone,
Reaching out to the community due to a failed inspection on a recent project in Los Angeles:
Did a conversion recently and we did not pass inspection due to the following reason: condenser and electric panel needed to be at least 20".
I have looked through the NEC and see the following clearance requirements:
1. Panel needs 30" width and 36" in front
2. There is a HVAC to yard setback requirement if db is at a certain level (ours is well below the db level)
3. There is a manufacturer's recommended working space on the equipment side (24")
Does anyone know where the code states a required 20" clearance between the condenser and electric panel?
Best regards!