OK, I hate to seem like I am anti-inspector, and for the record I am not. I find the vast majority of inspectors to be professional, concerned about doing a good job, and reasonable. Having said that, I just don't know what to do with an inspector that does what this one just did.
Shows up for the inspection, I explain briefly what we just did, he says OK, takes a look at the work and then grabs the #4 feed to the panel (we just replaced the feeders, not the panel). He says that the feeder seems warm to the touch and that it must be over loaded. I feel the wire and it feels room temperature to me, maybe slightly warmer which is no surprise. He says he wants me to put a probe on it and measure the current. I don't happen to have an amprobe on me but I point out that the #4 is good for 100 amps and there are only 6 breakers in the panel...two 2P 30s connected to non-continuous loads, two 2P 20s connected to non continuous loads and two 15a general circuits. The biggest loads, the 2 2P 30s are connected to heaters which aren't even on at the time so it would be virtually impossible for any perceived temperature increase to be due to overloading.
He says he's not comfortable with it and writes on the job card that we need to install a panel rated for the loads! I explain the the panel he is looking at is rated for the present loads and he just says "I'm not comfortable with it" and walks away.
How the heck do you deal with a guy like this? I'm sure I can go up a level and get the signature, but it's such a waste of time.
Shows up for the inspection, I explain briefly what we just did, he says OK, takes a look at the work and then grabs the #4 feed to the panel (we just replaced the feeders, not the panel). He says that the feeder seems warm to the touch and that it must be over loaded. I feel the wire and it feels room temperature to me, maybe slightly warmer which is no surprise. He says he wants me to put a probe on it and measure the current. I don't happen to have an amprobe on me but I point out that the #4 is good for 100 amps and there are only 6 breakers in the panel...two 2P 30s connected to non-continuous loads, two 2P 20s connected to non continuous loads and two 15a general circuits. The biggest loads, the 2 2P 30s are connected to heaters which aren't even on at the time so it would be virtually impossible for any perceived temperature increase to be due to overloading.
He says he's not comfortable with it and writes on the job card that we need to install a panel rated for the loads! I explain the the panel he is looking at is rated for the present loads and he just says "I'm not comfortable with it" and walks away.
How the heck do you deal with a guy like this? I'm sure I can go up a level and get the signature, but it's such a waste of time.