I was failed on an inspection yesterday, so maybe you all can shed some light on this.
2011 code cycle. Overhead service, my service conductors are landed in the meter can, and thru the back of the meter can into the MDP. I installed a ground rod and ran the GEC in 1/2" PVC into the meter can. I land it in a lug and from there run it to the MDP where the neutral and ground bars and MDP are bonded by the green bonding screw.
He fails it.
He wants the GEC to bypass the meter can and go thru the exterior wall and into MDP directly. He also wants a ground bar kit screwed into the exterior wall where the GEC will pass thru unprotected and continuously and into the house. Is there something to this? Should I get out of the trade?
2011 code cycle. Overhead service, my service conductors are landed in the meter can, and thru the back of the meter can into the MDP. I installed a ground rod and ran the GEC in 1/2" PVC into the meter can. I land it in a lug and from there run it to the MDP where the neutral and ground bars and MDP are bonded by the green bonding screw.