Re: Failed wall inspection for installing cut in box in fire
Paul
I'll have to look up the beginning of chapter 7 when I get back to the office on Monday. And you guys thought that inspectors couldn't be seperated from their code books.
Anyway, in chapter 7 it does mention penetrations as being protected by a tested system, however the exception allows steel outlet boxes to be installed without protection. I should have posted the section number.
Someday I think everyone is supposed to be on the ICC, at least that was the intent of merging the big three codes together. Of course CA will be one edition behind.
Sam
The hose stream test does not correlate to a firefighters hose. When an assembly is tested, it is exposed to fire in an oven for the specified time, such as 1 hour. The assembly is then removed and sprayed with a hose. The assembly has to maintain integrity to obtain the 1 hour rating. The details of flame temp, water pressure I don't remember, but that's the gist of it.
Rodger
The architect chooses the assembly to use in the design of the bldg. The UBC has some, UL has hundreds, and there are others. As long as the assembly is classified (not listed) by a NRTL then it will be approved by the bldg dept. Assemblys are classified (at least by UL) because it has to be constructed in the field whereas a circuit breaker is completely assembled when it leaves the factory. The UBC requires penetrations to be tested to a UBC standard which mirrors the UL standard for the same. I do not believe the word listed is used.
Bob
Your right, UL is not mentioned in the UBC. In the UBC, UL is not very big. ICBO (International Conference of Building Officials) and UL did not play well together in the past. I asked the question at seminars and got the shuffle off. However maybe this has changed with the ICC.