so, 2nd time this failed
1st time, we had the main incoming ground from building footer attached to the factory provided mount on the meter can neutral bar, thereby bonding the ground and neural in the meter enclosure. inspector didn’t like that, said meter can needs to be disconnected, and ground split 3 ways, run to each disconnect.
2nd attempt, failed it again with comment “same as before”
are we wrong in splitting the ground in the meter enclosure and running it to the disconnects below? in my eyes it was correct the first time around, but i’m not the inspector. any advice helps, since the inspector is useless.
1st time, we had the main incoming ground from building footer attached to the factory provided mount on the meter can neutral bar, thereby bonding the ground and neural in the meter enclosure. inspector didn’t like that, said meter can needs to be disconnected, and ground split 3 ways, run to each disconnect.
2nd attempt, failed it again with comment “same as before”
are we wrong in splitting the ground in the meter enclosure and running it to the disconnects below? in my eyes it was correct the first time around, but i’m not the inspector. any advice helps, since the inspector is useless.