failing inspection due to bond on 3 gang meter can

One way would be to bond the neutral in the gutter and then start the EGC there and not install an MBJ in each disconnect, but the code specifically requires it, so the method I mention is forbidden.

If I cared a little more, I would submit a proposal to add an exception for that very instance
Yeah there are a couple ways this could be handled. One might be just to require it for services with multiple disconnects. I guess the problem there is there isn't necessarily a gutter or box where the conductors are split. For example just picture two risers each going to a separate meter and disconnect. What about separating neutrals and grounds after the meter? Or maybe some language about you split them at the first available box or cabinet.
 