Fall of Potential Test Results

MatthewEE

Member
Location
Maryland
Occupation
Engineer
I'm reviewing test results from a contractor who claims to have done a fall-of-potential test at a ground test well. The readings are taken at ten foot intervals, from 10ft to 100ft, with results starting at 1.10 ohms (10ft), a bunch of 1.00 ohms (20ft-80ft), then 0.90 ohms at 90ft and 100ft. These results aren't like any I've ever seen for a fall-of-potential test. I typically see a sharp upward curve in resistance values around 60ft or so. Is it just me, or do these results seem dubious?
 
Is there any buried metal, like a storage tank, in his measuring path.
Is this undisturbed soil or has it been compacted or filled?
 
This is a new aircraft hangar with a large ground grid of buried wire and rods. But I don't know which direction they went with the test probes.
 
This is a new aircraft hangar with a large ground grid of buried wire and rods. But I don't know which direction they went with the test probes.
I would be surprised if they were able to find undisturbed earth within 100' of the hanger.
Are you trying to find the actual resistance to ground or just develop a baseline database?
 