Re: Falling GRS Conduit
While not disagreeing with Don, let me start out by saying that we have miles of PVC Coated GRC from all of the big 3, [Ocal, PermaCote, & Robroy]. We have standardized on it for all of our exterior locations. We have had this situation, but only in limited amount. Here's what we found; vertically mounted strut, [open ends up and down], with horizontally running conduit, and factory clamps. All components manufactured by the same manufacturer in the area of concern, all of the same line & spec. In a few locations, during the summer, [ warm & things like to expand], in a couple of areas, we have had PROPERLY installed PVC coated hangers slip free from the strut. These areas are adjacent to lightly loaded traffic ramps. In one location, it happened twice over the period of a year. All was installed properly. Our crew was certified by OCAL. We changed strut straps, and all was tight. In one location only, did we find hat it happened a second time, a few months later. We can only surmise that there were differences in the thickness of the coating, between the strut, pipe, and straps. When exposed to prolonged sunlight and warmth, accelerated by road vibrations, these lack of tolerances were different enough to allow for this. All fittings, pipe, and the like were of one manufacturer, and correctly sized. If this is what is happening here, and all has been installed properly, I would contact the manufacturer of the materials, and let them investigate, and possibly pay to have this work redone, should inconsistencies in their system be found. [If that is what Don as intimating, then he would be correct]. We have found them quite forthright on occasion where they were at fault. What is of concern to me is that this seems to be happening in such a widespread fashion in this one area. While there may be additional input added with respect to hanger spacing, a manufacturers' parts must comply with their own published data.