Good pictures Roger!! (And some people say we're not nice enough )
Bob & Larry:
I guess its a good thing the engineer didn't specify 3 parallel sets of cable as the primary feeder. It would be a real PITA to try and split that third wire in half!!
I240.8 allows parallel circuit breakers where they are factory assembled in parallel and listed as a unit. 310 doesn't say parallel sets have to land on the same device, but it does say they have to be electrically connected at both ends. I am starting to think these are two separate feeders, but then the OCP at the source would be too large??
Steve
Bob & Larry:
I guess its a good thing the engineer didn't specify 3 parallel sets of cable as the primary feeder. It would be a real PITA to try and split that third wire in half!!
I240.8 allows parallel circuit breakers where they are factory assembled in parallel and listed as a unit. 310 doesn't say parallel sets have to land on the same device, but it does say they have to be electrically connected at both ends. I am starting to think these are two separate feeders, but then the OCP at the source would be too large??
Steve