Sean.Day72
Member
- Location
- Florida
Recently installed a Nema 4X stainless steel enclosure at a remote slide gate location for access control. The internal temperature is reaching in the box 130F and its causing the UPS to fail. It is an APC UPS rated 104F. We have proposed to install a solar shield over the box and upgrade the UPS to a SOLA HD ups rated for 120F. We are also proposing to install a 24V fan kit with a retrofit louver to keep air circulating in the box. There will be a drip hood over the louvers to protect from driving rain. This is down here in Florida, will putting the louvers/fan kit into the box cause any humidity issues? The box is currently completely sealed up, but I feel the humidity can still get in there regardless? I want to see if there are any other issues I should be worried about? Mentioned to get a box with an A/C but at this point that would be pain to replace and I feel overkill for the equipment inside. I've used Air Conditioned boxes for SCADA control panels and at traffic light controls, but this box is pretty dinky compared to that stuff. If there any other solutions to cool down an outdoor box I'm all ears.
Box is 30"x24"x12" with Hardened Ethernet Switch (160F), Fiber Patch Panel, Doors Controllers (160F), 24VDC Power Supply (150F), and UPS(104F)
Box is 30"x24"x12" with Hardened Ethernet Switch (160F), Fiber Patch Panel, Doors Controllers (160F), 24VDC Power Supply (150F), and UPS(104F)