frankft2000
Senior Member
- Location
- Maine
The wording in the previous code allowed for the use of a standard fan box as long as the fan was hung independently from the box. A 2x6 behind the box and you are good to go. I use 3" screws thru the bracket to the wood behind the box. This new ruling does not seem to support that if you use a 3 wire cable but does support it with a 2 wire cable.
I agree with what you wrote, but splitting hairs here. Would the Arlington brand fan rated boxes still be legal, since the mounting screws don't actually tie into the box, rather they just pass through to get to the building structure?