Commercial application out on open patio and have to hang ceiling fans. I know the box must be fan rated and damp location listed. There must be a box to do just this.
Yeah its exposed. I was wondering if there was such a box for my application.Dennis Alwon said:chevy, if the box is exposed then just use a wp round box and mount the fan with screws to the framing above , not to the box. If the box is recessed in sheetrock then it is not an issue just use a standard fan box.
chevyx92 said:Yeah its exposed. I was wondering if there was such a box for my application.
stickboy1375 said:The only box for your application is a bell box, like Dennis mentioned above... Check out sections 422.18 (A) & (B)
Exactly what I used. I mounted the box via the mounting ears with two 1" wood screws into one 2x8, and placed the two 1/4" lags supporting the fan bracket into the other 2x8. All hardware was stainless steel.Dennis Alwon said:Just use one of these
![]()
LarryFine said:All hardware was stainless steel.
Sounds like a WP Fan Rated Box doesn't exist. There's money to be made.stickboy1375 said:The only box for your application is a bell box, like Dennis mentioned above... Check out sections 422.18 (A) & (B)