winnie said:
Pop quiz:
A 120/208 4 wire feeder from a wye source feeds a panel. The panel is fully loaded with a large heater connected from the A leg to the B leg, with 120V loads fed between the C leg and the neutral. Is the neutral a 'current carrying conductor'.?
-Jon
I like your quiz because it’s so easy to answer the wrong way.
You ask about
the neutral and using the term neutral for all grounded conductors.
First
The problem with saying
the neutral is that there is no such thing. . There are 2 types of grounding conductors, equipment bonding/grounding and electrode earthing/grounding, that are grounding throughout the system. . There is an ungrounded conductor that is ungrounded throughout the system. . But there’s no such thing as a neutral that is neutral throughout the system.
Neutral is a
condition not a category label that applies thruout the system. . The common connection point of a wye transformer is grounded
and neutral. . The conductor connected to that common point and brought to the service is grounded
and neutral. . The conductor connected to that common point and feeding a subpanel is grounded
and neutral. . The conductor connected to that common point and part of a multiwire HR, that has all hot conductors of the system present, is grounded
and neutral. . The conductor connected to that common point and part of a HR, that does
not have all hot conductors of the system present, is grounded
but not neutral. . So a grounded
neutral commonly enters a junction box, grouped in the same circuit run with all of the hot conductors, and be connected to other grounded conductors that are
not neutrals.
An ungrounded conductor is always ungrounded throughout the whole system.
A grounding conductor [electrode or equipment] is always connected to ground throughout the whole system.
A grounded conductor is always grounded throughout the whole system.
But a neutral conductor is
not always neutral throughout the whole system.
Neutral is a condition that applies to the grounded conductor is some places but
not in other places.
Secondly
The problem with using the term ‘neutral’ instead of grounded. . There is current carrying and then there’s current carrying but unbalanced current only. . The code treats them differently.
winnie said:
Is the neutral a 'current carrying conductor'.?
Yes the neutral is always current carrying but the word ‘neutral’ means it’s also unbalanced current only. . Is the grounded conductor actually a neutral at the point you ask about in your question ? . On the 120v circuits [of a 120/208 wye] the answer is
no. . The T310.15(B)(2)(a) count specifies unbalanced current only current carrying conductors [310.15(B)(4)] so that wouldn’t apply to grounded conductors in those 120v circuits.
David