a 200amp 1ph breaker in an enclosure is installed under a meter for a chicken house.4/0 urd (2) hots and a neutral are installed (100')from this breaker to a 42 cir mb panel in the chicken house.
a ground rod is installed and the neutral is bonded in this panel all neutrals and grounds land on the neutral bar.approx. 2' of pvc conduit is installed from this panel to a 100amp breaker and enclosure and is tapped off of the 200amp mainbreaker terminals with #2 urd.the feeder then leaves the 100amp breaker enclosure (2) hots (1) neutral no ground (#2 urd aluminum) and extends to a 12 cir main lug panel for lights and fan receptacles,located in an opensided silage storage building approx. 100',a ground rod is driven and the neutral is bonded to the can once again,all neutrals and grounds are on the same bar. should a ground wire have been pulled with the feed to the panel at the silage barn or not?should a main disconnecting means been installed in the main lug panel even though the 100 amp main breaker is in the chicken house?
a ground rod is installed and the neutral is bonded in this panel all neutrals and grounds land on the neutral bar.approx. 2' of pvc conduit is installed from this panel to a 100amp breaker and enclosure and is tapped off of the 200amp mainbreaker terminals with #2 urd.the feeder then leaves the 100amp breaker enclosure (2) hots (1) neutral no ground (#2 urd aluminum) and extends to a 12 cir main lug panel for lights and fan receptacles,located in an opensided silage storage building approx. 100',a ground rod is driven and the neutral is bonded to the can once again,all neutrals and grounds are on the same bar. should a ground wire have been pulled with the feed to the panel at the silage barn or not?should a main disconnecting means been installed in the main lug panel even though the 100 amp main breaker is in the chicken house?