Strathead
Senior Member
- Location
- Ocala, Florida, USA
- Occupation
- Electrician/Estimator/Project Manager/Superintendent
I'm with Wayne. 480 corner grounded. That will reduce the cost of panels and feeders since you don't have to bring the 4th wire.
The OP said 480/240 3Ph 4W Center Tapped delta not 480V 3PH 3W corner delta, so the service needs 4W.I'm with Wayne. 480 corner grounded. That will reduce the cost of panels and feeders since you don't have to bring the 4th wire.
thanks...I read that incorrectly and you are 100% correct.How's that?
With a 480V corner grounded delta, you only have 2 ungrounded conductors and could conceivably use panels with just 2 buses. But both 480/240V delta and 480Y/277 have 3 ungrounded conductors required to get 480V delta 3-wire to supply the motors.
Cheers, Wayne
not the best idea if there are VFDs involved.I'm with Wayne. 480 corner grounded. That will reduce the cost of panels and feeders since you don't have to bring the 4th wire.
I hope penny pinching isn't involved at this point.I'm with Wayne. 480 corner grounded. That will reduce the cost of panels and feeders since you don't have to bring the 4th wire.
Yeah, it's an oddball for sure. I have heard of it, but never seen it in the wild. I don't see the point, because sure, you get 240V single phase, but no 120V, so you STILL need another transformer for that. So what have you really saved?
Especially on a farm where there tends to be non qualified working on things after initial install. 277 to ground is bad enough but 480 to ground is even worse. High leg isn't much better as it is 416 to ground. But we do have quite a few of those around here for more limited loads and they are supplied via open delta banks.Absolutely not a corner ground! Not a fan, nope, no way.
The OP said 480/240 3Ph 4W Center Tapped delta not 480V 3PH 3W corner delta, so the service needs 4W.
In any case you never need to run a feeder neutral unless the load requires it.
First, off I misspoke. You do have to run the neutral at the service, if it exists, but since I can't find the code right now, I think that may just be for a 4 wire wye service. Either way, the OP didn't appear to be saying he needed the center tap. So my post was to suggest that he not have a center tap provided.The OP said 480/240 3Ph 4W Center Tapped delta not 480V 3PH 3W corner delta, so the service needs 4W.
In any case you never need to run a feeder neutral unless the load requires it.
You must run the "grounded conductor" to the service disconnect or first for any voltage system whether it is a neutral conductor or not.First, off I misspoke. You do have to run the neutral at the service, if it exists, but since I can't find the code right now, I think that may just be for a 4 wire wye service. Either way, the OP didn't appear to be saying he needed the center tap. So my post was to suggest that he not have a center tap provided.
Yep. As I said earlier, NO version of Delta is good if you ever want to use VFDs. It CAN be done, but it is a recipe for trouble.not the best idea if there are VFDs involved.