Had a discussion with some clients and other electrician. They have a new project where they install a animal dryer, they say pull about 13 amps. It will basically be at one location at the sink area. I informed them the most likely will have to have a dedicated circuit, especially if it is 'fastened' in place even if it is cord and plug connected, plugged into a duplex receptacle, (technically a code violation in my opinion on a 20amp branch circuit can only supply single receptacle not duplex will have to gfci protection another way). There was push back and stated that its not needed and they 'do it ' all the time.
Am I missing something on the definition of 'fastened in place'? Only definition I have found is Article 625, not in 100 of the NEC 2020. They did say the dryer is 'secured' to wall and it draws 12.7 amps (basically 13 amps). Thats more than 50% of the branch circuit rating, so no other outlets (other receptacles in this case) can be supplied by it per NEC.
Am I missing something on the definition of 'fastened in place'? Only definition I have found is Article 625, not in 100 of the NEC 2020. They did say the dryer is 'secured' to wall and it draws 12.7 amps (basically 13 amps). Thats more than 50% of the branch circuit rating, so no other outlets (other receptacles in this case) can be supplied by it per NEC.