FAU QUESTION???

Status
Not open for further replies.

joeyman

New member
The HVAC guy is having some issues with his thermostats burning out and he blames it on the way the furnace was wired. It's a normal 110v residential furnance powered by a 3 wire cord pluged into a normal receptacle. Is it possible for a low voltage thermostat to be burned out by the way the furnace is wired. Also we tested the receptical which reads 120v. (Proper installation)
 
Re: FAU QUESTION???

I dont think so, But is a furnace listed for wiring via plug and cord?

I know this would be a good way in an area that is prone to loosing power allot as it would allow an easer way to power it from a generator. I'm just not sure it is the correct way?

Now don't tell anyone but my own furance has a male pig tail that sticks out of the switch box and the switch is a 3-way which when it is up it's on house power but when it's down it's on the pig tail for generator. :p

[ August 24, 2004, 09:23 PM: Message edited by: hurk27 ]
 
Re: FAU QUESTION???

He probably has a defective trans in the furnace,ask him to check the secondary voltage from the trans..normaly it should be near 24 volts
 
Re: FAU QUESTION???

joeyman,
Some of the newer furnaces with the diagnostic boards have a diagnostic code that indicates reverse polarity either at the transformer primary or secondary. Now I have seen where this code will appear many years after installation, after a board failure. The unit in question (Goodman/Janitrol) was in fact wired correctly for 7 years, the code was a malfunction of the board. Maybe he got a "reversed twinnings" code and is trying to blame you.
Brian
 
Re: FAU QUESTION???

But to say that it is causing the stat's to burn out? Thats a far cry. I just cant see this with a isolated power supply (24v 40ma) Somthing must be wired wrong on the low voltage side for this to happen if it's not a bad/wrong transformer.
 
Re: FAU QUESTION???

Check the neutral connections.That simple thing has sent 240 through many circuits when a neutral is shared from circuits on 2 phases.
 
Re: FAU QUESTION???

Hey Hurk I have the same idea for my furnace (for generator hook up) Only problem is my generator has a bonded neutral so I will need to switch the neutral. DO they make a double pole three way switch?
 
Re: FAU QUESTION???

The HVAC guy is having some issues with his thermostats burning out
I wonder exactly what he means by "burning out"?

If the low-voltage thermostat in question has a "heat anticipator", it can be burned open by some testing procedures. The heat anticipator element is designed to be in series with the contacts, and the load (relay coil, zone valve, etc) being switched.

I've seen many thermostats that have been ruined by inadvertantly shorting out the load while trying to test the relay by bypassing (shorting out) the thermostat contacts.

Ed
 