Saturn_Europa
Senior Member
- Location
- Fishing Industry
- Occupation
- Electrician Limited License NC, QMED Electrician
The VFD is for a large Reverse Osmosis pump. The motor was replace about 3 months ago. The pump has about 2 weeks of run time on the new motor. The new motor is the same name plate amps and hp. Rotation has been confirmed.
The drive has faulted 3 times on start up with the error code Fault F9 Trnsistr OvrTemp. Power cycling the drive and starting it after a few minutes has allowed the unit to operate. I tried using the reset button on the drive panel and but it would immediately fault.
None of the drive parameters have been changed since commissioning. Parameter 35 [Motor Control Mode] is set to 1 – Induction SV.
Rockwell Automation Knowledge base recommends doing an autotune among other things:
Rockwell Automation Knowledgebase
The instructions in the manual for Auto Tune are a little unclear to me. Uncoupling the motor from the pump is not an option.
Auto Tune is on Page 61 of the manual: PF 750 Manual
Is autotune the right path to go down? The drive does not fault during operation. It faults immediately on start up.
Its a critical piece of equipment and right now we are discussing just leaving it running and letting the extra water go over the side when demand drops.
The drive has faulted 3 times on start up with the error code Fault F9 Trnsistr OvrTemp. Power cycling the drive and starting it after a few minutes has allowed the unit to operate. I tried using the reset button on the drive panel and but it would immediately fault.
None of the drive parameters have been changed since commissioning. Parameter 35 [Motor Control Mode] is set to 1 – Induction SV.
Rockwell Automation Knowledge base recommends doing an autotune among other things:
Rockwell Automation Knowledgebase
The instructions in the manual for Auto Tune are a little unclear to me. Uncoupling the motor from the pump is not an option.
Auto Tune is on Page 61 of the manual: PF 750 Manual
Is autotune the right path to go down? The drive does not fault during operation. It faults immediately on start up.
Its a critical piece of equipment and right now we are discussing just leaving it running and letting the extra water go over the side when demand drops.