- Illinois
- retired electrician
Re: Fault current and fuse protection
ron,
Don
ron,
But if the fault current that you are using in your calculations is higher than what is actually available, your clearing time may be faster than it should be and that would result in a lower incident energy. That is why I say that where the available fault current is not actually known that you should start with an infinite bus current and work down in steps to find the maximum incident energy. Because higher fault currents may generate faster trip and clearing times, often a lower fault current will have a higher incident energy requiring a higher level of PPE.Unfortunately, I have to consider clearing time of OCPD on the calculated arc flash fault current, and I start with whatever the POCO gives (many times it is infinite primary which I calculated myself without their help first) and hope as I work through distribution transformers throughout the facility, I'm coming closer to a real available fault current and impedance to continue the calc further (and hopefully more accurately) with the more refined information.
Don