Fault Current/ Breaker Operation

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Those breakers will not open as they will not see the fault current. Typically a fault at that location will not open any overcurrent device and will "burn" open after some time.
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
The fault current will return to the Source which is above the top of your schematic. The Circuit Breakers you have indicated won't "see" the fault current.
 