charlie b said:OK. I have looked at the utility's fax. It has blank spots that are filled in by hand. One of these is "ultimate" fault current.
I am not certain exactly what is represented by the phrase, ?ultimate 171,800 amps symmetrical at 240 volts.? But it certainly has nothing to do with the fault current available at a specific user?s transformer location. As evidence, I offer the fact that a city in Houston (served by the same utility company as the OP is discussing) has published a list of requirements related to permits and construction. Here it is (copy into browser to view the document):
[FONT='Arial','sans-serif']www.bunkerhill.net/Government/Permits/Contractor%20Permit%20Package%20122007.pdf[/FONT]
On page 18 of that document, it declares that the local utility?s value of ultimate fault current, for single or three phase, is 171,800. So clearly that number is not related to any given installation.
The number you should be using as the basis for the rating of any equipment within your building need be no higher than the 12,300 amps that the utility shows as ?initial fault current.?
Charlie,
The formula sheet that was given to me and the one I faxed you some how forms a number the inspector is looking for. Is the 12,300 number you gave as the initial fault current based on the formula sheet? thanks