Fault Current:
EC - retired
Reply I received when I asked about fault current available:
Current 37.5 KVA Transformers
At 277V ? 5250A L-G
At 480V ? 3000A L-G
Uprate 100 KVA Transformers
At 277V ? 11900A 3 Phase L-G
At 480V ? 6850A 3 Phase L-G
It is a 277/480 Y. How does the 480v L-G work into this?
At 277V ? 5250A L-G
At 480V ? 3000A L-G
It is helpful to know the impedance (%Z) of each transformer. However, if you figure 5% just for this conversation you'll get the following:
37.5kVA / (.831 x .05) = 902.5AIC (3-phase). To get the L-G values you divide by 3. Not sure where 3000A is coming from, unless my math is off. Also, 480V is typically a phase-phase value, not phase to ground.
That is my issue...480v L-G.