How is one supposed to find the available fault current?
How is one supposed to find the available fault current?
Since you didn't elaborate on what the spplication was Start by asking the POCO.
that will tell you what it is at the terminals of the POCO xfmr. Ohm's law will tell you what it is downstream.
Bussmann has a nice fault current app, but you still need info from the utility to start with. You need either the available fault current or the kVA and impedance of the transformer (infinite bus). Then you can build your network and see the available fault currents at each point on the network.
That is correct....the app has a provision to add motor contributions.With an industrial/commercial facility that is where I would start also based upon a transformer to also include a 100% motor contribution.
That would require a fault current coordination study which commonly is done by a qualified person such as a PE.
What the OP asked was a loaded question which did not include any clue as to if it were residential, commercial, industrial facility, or?
What would be the simplest answer to a residential facility, would using ohms law be a used?
The fault current downstream is going to be whatever it is at the POCO xfmr terminals and gets reduced as it goes downstream because of the increased impedance mostly due to the resistance of the conductors. This is not something that requires any kind of study to calculate for most simple cases.
Granted, it can become convoluted if there are motor contributions and downstream transformers to consider, but even so, in most cases, it is not all that hard to make a reasonable estimate of the available fault current at any point in the system.
What is much more difficult, and requires at least someone with some experience and training, is to calculate the incident energy that might be available at a point downstream. But they are two completely different and almost unrelated calculations.
I don't really know, but my guess would be his concern is 110.24....
But, is this the concern of the OP? Does anybody know?
The transformer on the pole is 37.5 kva. I just want this calc to beable to put the info on a plaque on the service. Just to satisfy the code.
Now you need transformer impedance and then you will at least be able to tell what available fault current is at the transformer terminals. Find conductor sizes, type, length and type of raceway, and the Excel calculator I mentioned earlier will make this one fairly easy to come up with a number.The transformer on the pole is 37.5 kva. I just want this calc to beable to put the info on a plaque on the service. Just to satisfy the code.
25kA?The 3 mains are 25000kv and the main breakers for the remote panels are also 25000kv. Can't find the fault currents on their web site