Fault Current

Status
Not open for further replies.

guschash

Senior Member
Location
Ohio
Trying to understand fault current. If the main breaker is rated for say 27000 fault current amps ,does all the other breakers in panel have to be rated at 27000 amps as well ?
 
The rating of the main breaker does not tell you the actual available fault current.

The downstream breakers must have an AIC rating at least equal to the available fault current at the line side of those breaker, of be, as Gus said, a listed series combination system.
 