Available where (e.g., at a building's service point or at a distribution panel within the building), and from what source (e.g., from a utility transformer, an on-site transformer, or a portable generator)?
 
paulnorris said:
How do I figure available fault current?
Based on what information? If you have a 3-phase transformer with impedance "Z", the available fault at the transformer will be:
kVA / (sqrt(3) * L-L kV * Z)

This is a conservative number as this assumes an infinite source bus. (The source impedance would reduce this number)

[edit: clarified formula]
 
Last edited:
waht Chalie b says..

but, pardon me, looking at your profile I can;'t help but say WHATTTTT ?????
we always call YOU :)
 
paulnorris said:
Thanks. I want to figure available fault current at the transformer. Example would be 45 KVA 277/480 3 ph 3.01 imp.
Then it would be 45 / (sqrt(3)* 0.480 * 0.0301) = 1798 amps

[edit: I used 0.0301 because Z is usually given in % so 3.01% = 0.0301]
 
Last edited:
Im surprised the power company doesn't have namograms or a computer program to perfom this calculation. ????
 
While this infinite bus calculation is great, it is of no use for arc flash analysis am I correct? Just checking.
 
GMIEE said:
While this infinite bus calculation is great, it is of no use for arc flash analysis am I correct? Just checking.
Correct, you need more info for the arc flash calculations.
 