How do I figure available fault current?
Based on what information? If you have a 3-phase transformer with impedance "Z", the available fault at the transformer will be:paulnorris said:How do I figure available fault current?
Then it would be 45 / (sqrt(3)* 0.480 * 0.0301) = 1798 ampspaulnorris said:Thanks. I want to figure available fault current at the transformer. Example would be 45 KVA 277/480 3 ph 3.01 imp.
Correct, you need more info for the arc flash calculations.GMIEE said:While this infinite bus calculation is great, it is of no use for arc flash analysis am I correct? Just checking.