Got called out to take a look a look at the aftermath of a fault on a 200A, 480V feeder. The fault occured in a water filled handhole between two phase conductors. None of the three upstream breakers tripped. Instead, the water actually came to a boil and the steam alerted people to a problem.
Naturally, the whole run will be replaced. But I'm wondering if the Instantaneous setting on the 200A MCCB, if set to something less than Max (as it was) would have at least cleared the fault.
I imagine the only sure way to catch such a fault is with ground fault which in this case was only on the 3000A main upstream and it didn't trip either.
Would setting the Instantaneous lower have done anything in this instance? How much current will flow through water. I guess it's a function of the distance so let's say 4 or 5 inches apart? Anybody know?
Thanks
Naturally, the whole run will be replaced. But I'm wondering if the Instantaneous setting on the 200A MCCB, if set to something less than Max (as it was) would have at least cleared the fault.
I imagine the only sure way to catch such a fault is with ground fault which in this case was only on the 3000A main upstream and it didn't trip either.
Would setting the Instantaneous lower have done anything in this instance? How much current will flow through water. I guess it's a function of the distance so let's say 4 or 5 inches apart? Anybody know?