Fault or Inrush Current?

Status
Not open for further replies.

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
I agree, it’s hard to see but a fault is what it looks like.
this come from Syncrowave?
if not, look at the event in syncrowave. It will give you a clearer picture.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Thanks, that's what we thought. But I'm puzzled why it settles down after only 2 cycles, and it looks like I have balanced (slightly increased) currents until the breaker opens at 9 cycles.

That’s what I was wondering when I looked at it. I expected it to be longer.
thats why I suggested SEL syncrowave. There you can see the phasers rotate through the fault.
two cycles almost seems like something falling through.

without knowing 51 pickups and curves I’m only guessing though.
im assuming it opened on 51N.

is fault locate on for this relay?
 

synchro

Senior Member
Location
Chicago, IL
Occupation
EE
I have no expertise in protective relaying, but isn't there a very large burst of zero sequence current (what in my world I'd call common-mode current) for a little over 1 cycle? So the current flows in-phase on all conductors for the duration of the burst. I'm not sure what kind of failure could cause this.
I agree that the voltage droop is mainly limited to phase C, so with that info alone I'd suspect a ground fault on that phase as mentioned above.
 

synchro

Senior Member
Location
Chicago, IL
Occupation
EE
Is it possible that the event is a closed transition transfer when there's some phase shift between the two sources? And maybe the balanced but somewhat increased currents after the big event is due to loads being picked up after the transfer happens.
 

JoeStillman

Senior Member
Location
West Chester, PA
That’s what I was wondering when I looked at it. I expected it to be longer.
thats why I suggested SEL syncrowave. There you can see the phasers rotate through the fault.
two cycles almost seems like something falling through.

without knowing 51 pickups and curves I’m only guessing though.
im assuming it opened on 51N.

is fault locate on for this relay?

I'm pretty sure that printout is from Synchrowave. This distribution is all underground downstream of this gear - about 50 transformers on 8 loops serving a college campus. The breaker that tripped is one of the mains in a main-tie-main arrangement. There is a 2MW combined-heat-and-power generator connected to this side of the bus via a wye-connected transformer. This breaker and all of the loops have (coordinated) ground-fault-instantaneous and that is what tripped in the main. None of the branches nor the generator tripped on ground fault. That would imply that the fault is on the substation bus somewhere, but there is no evidence of an arcing fault inside this brand-new switchgear.

The utility relays upstream have no instantaneous GF - just very-inverse. I've proposed eliminating the instantaneous on this main as well. The POCO has to approve a change in relay settings and they've promised to get back to me - in EIGHT WEEKS!

I think it's possible that this was a ground-fault on the line upstream and the generator fed the GF current. POCO ignored it because no 50G, only 51G. I wish I could tell from the Synchrowave what direction the current was going.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
I'm pretty sure that printout is from Synchrowave. This distribution is all underground downstream of this gear - about 50 transformers on 8 loops serving a college campus. The breaker that tripped is one of the mains in a main-tie-main arrangement. There is a 2MW combined-heat-and-power generator connected to this side of the bus via a wye-connected transformer. This breaker and all of the loops have (coordinated) ground-fault-instantaneous and that is what tripped in the main. None of the branches nor the generator tripped on ground fault. That would imply that the fault is on the substation bus somewhere, but there is no evidence of an arcing fault inside this brand-new switchgear.

The utility relays upstream have no instantaneous GF - just very-inverse. I've proposed eliminating the instantaneous on this main as well. The POCO has to approve a change in relay settings and they've promised to get back to me - in EIGHT WEEKS!

I think it's possible that this was a ground-fault on the line upstream and the generator fed the GF current. POCO ignored it because no 50G, only 51G. I wish I could tell from the Synchrowave what direction the current was going.

You should be able to with the phasor rotations. Did you get the full event file or just that snapshot?
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
This breaker and all of the loops have (coordinated) ground-fault-instantaneous and that is what tripped in the main. None of the branches nor the generator tripped on ground fault.

that would explain the short duration.
is the 50 in the SER?

maybe look at the 1/4 cycle event data if it’s available. It will also give you degrees and you will be able to see the reverse flow
 

JoeStillman

Senior Member
Location
West Chester, PA
that would explain the short duration.
is the 50 in the SER?

maybe look at the 1/4 cycle event data if it’s available. It will also give you degrees and you will be able to see the reverse flow

Yes, 50N in the SER. I have a bunch of files I can't read: they're called CEV_L1.CEV thru CEV_L_4.CEV. I can open them with XL if I rename them to *.CSV but it's all gibberish to me.

I'm sure somebody has the quarter-cycle event data. Is that somewhere in the CEV files?
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
1
 

Attachments

  • F5F8E1C8-9475-43A1-A4C7-F3C3BF541F92.jpeg
    F5F8E1C8-9475-43A1-A4C7-F3C3BF541F92.jpeg
    113 KB · Views: 3

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
From what I’ve seen, I think so also, it just needs to be concrete evidence.

It would be great to see the phasor rotate through the fault. It looks like it, but during a fault the currents go all over the place. Upper right, little clock symbol, move the time back and forward a little to see the phasor movement. You can specify the time also.

I only say this because when you take the evidence to the POCO you need to have your stuff 100% to prove it.

get a phasor screen, then drag the cursor through the event to see the phasor rotate, you should be able to see it change direction from CCW to CW. Upper right, make sure rotation setting is set correctly though.
 
Last edited:

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
You may have this figured out already...
what about adding or turning on a 67 element to your trip equation?
just “and” it with the overcurrent maybe?
 

mivey

Senior Member
Inrush would be full of 2nd harmonics. If the the voltage increase preceeds the current increase the problem should be before the relay and the system is reacting to a voltage surge. A fault beyond the relay should see a voltage drop first then a current surge following.
 

JoeStillman

Senior Member
Location
West Chester, PA
It would be great to see the phasor rotate through the fault. It looks like it, but during a fault the currents go all over the place. Upper right, little clock symbol, move the time back and forward a little to see the phasor movement. You can specify the time also.

I only say this because when you take the evidence to the POCO you need to have your stuff 100% to prove it.

get a phasor screen, then drag the cursor through the event to see the phasor rotate, you should be able to see it change direction from CCW to CW. Upper right, make sure rotation setting is set correctly though.

I was able to make an animated GIF showing the orange cursor sweeping across the fault. You can see the current phasor swing around 180° and back. Tried to upload it but the forum software doesn't like my file.

https://filebin.net/t5aay0tzd7t09fr2...GIF?t=015zj9u9
 
Last edited:

synchro

Senior Member
Location
Chicago, IL
Occupation
EE
I was able to make an animated GIF showing the orange cursor sweeping across the fault. You can see the current phasor swing around 180° and back. Tried to upload it but the forum software doesn't like my file.

https://filebin.net/t5aay0tzd7t09fr2...GIF?t=015zj9u9

Nice. Definitely shows the complete 180 reversal in the phase C current.

Do you know if there's a separate current transformer for the neutral, or is the neutral current derived from the sum of the line currents (using a physical connection of CTs or software)? The reason I mention this is that in your original post the neutral current (and also IG) is in phase with all of the line currents. Even if there's reverse current flow from another source I would expect Kirchoff's law that all currents sum to zero would still apply. If there's a separate CT for neutral, is it possible the polarity is reversed somehow and this could cause an erroneous ground fault detection because the measured neutral current would not (at least partially) cancel out the measured line currents. I'm not very conversant in MV hardware so if I'm full of it let me know :blink:
 

JoeStillman

Senior Member
Location
West Chester, PA
Nice. Definitely shows the complete 180 reversal in the phase C current.

Do you know if there's a separate current transformer for the neutral, or is the neutral current derived from the sum of the line currents (using a physical connection of CTs or software)? The reason I mention this is that in your original post the neutral current (and also IG) is in phase with all of the line currents. Even if there's reverse current flow from another source I would expect Kirchoff's law that all currents sum to zero would still apply. If there's a separate CT for neutral, is it possible the polarity is reversed somehow and this could cause an erroneous ground fault detection because the measured neutral current would not (at least partially) cancel out the measured line currents. I'm not very conversant in MV hardware so if I'm full of it let me know :blink:

Thanks! The original post was copied from somebody else before I had SynchroWave, so I don't know if they are showing a calculated residual neutral or the measured zero-sequence CT that all the phase conductors pass through.
 