Hello anyone
I am looking at a power system, running at 6.6kV, where the designer is proposing to use parallel cables to feed from the HV switchboards. I have calculated a minimum core size for the cable based on the prospective fault currents that will occur of about 70sqmm.
The designer is proposing to use 2 off of approximately 50sqmm in parallel to achieve this figure. My understanding is that, regardless of the loading the minimum cable size must be 70sqmm. Therefore he needs to use 2 off 70sqmm otherwise the cable will not survive the potential fault current if a single cable fails.
Has anyone any thoughts on this?
I am looking at a power system, running at 6.6kV, where the designer is proposing to use parallel cables to feed from the HV switchboards. I have calculated a minimum core size for the cable based on the prospective fault currents that will occur of about 70sqmm.
The designer is proposing to use 2 off of approximately 50sqmm in parallel to achieve this figure. My understanding is that, regardless of the loading the minimum cable size must be 70sqmm. Therefore he needs to use 2 off 70sqmm otherwise the cable will not survive the potential fault current if a single cable fails.