hello21
Member
- Location
- san francisco
Hi,
My understanding of a typical delta-wye step-down transformer is that the primary and secondary windings are electrically isolated, and you are inducing a current in the secondary windings using an alternating magnetic field. But what happens when there is a fault in the secondary?
A line to ground fault on the secondary side of the transformer, the fault current should make its way on the equipment ground back to the XO of the transformer then go on the phase conductor and hopefully trip out a breaker (usually the closest breaker to the fault if appropriately coordinated).
I expect line to line faults to behave similarly, except fault is propagating on phase conductors only.
I assumed that the fault current would not be induced in the primary, and so regardless of the fault type and magnitude, the primary side of the transformer would not see a fault. Am I way off here?
My understanding of a typical delta-wye step-down transformer is that the primary and secondary windings are electrically isolated, and you are inducing a current in the secondary windings using an alternating magnetic field. But what happens when there is a fault in the secondary?
A line to ground fault on the secondary side of the transformer, the fault current should make its way on the equipment ground back to the XO of the transformer then go on the phase conductor and hopefully trip out a breaker (usually the closest breaker to the fault if appropriately coordinated).
I expect line to line faults to behave similarly, except fault is propagating on phase conductors only.
I assumed that the fault current would not be induced in the primary, and so regardless of the fault type and magnitude, the primary side of the transformer would not see a fault. Am I way off here?