You just said:
http://forums.mikeholt.com/showthread.php?t=192495&page=3&p=1928465#post1928465
If the supply was wye, the trafo wouldn't automatically be a wye primary. Almost all 600 volt dry types are delta wye or delta delta. All off the the shelf 480:480/277Y isolation are delta wye. No engineer, if seeking isolation, is going to order a none standard unit just because the 480 volt service is solidly grounded. You keep implying that if the trafo was for isolation, it would have been Y:Y and not delta wye. Not the case, nothing about isolation stops a delta wye.
I'm not talking about ungrounded systems. I'm talking about a delta primary and wye secondary trafo.
What I was referring to was this:
Delta wye isolation would require 3 wires + ground primary feed.
Wye wye isolation would require 4 wires + ground primary feed.
So you do save a wire by having a delta primary isolation transformer.
Very true, thank you, which is why that isolation was delta wye and not wye wye.