Here is a rough draft of a proposal I am considering for the FBC. Any comments or opinions?
Text of Modification [additions underlined; deletions stricken]:
Revise Section Title: Section R313 Smoke Alarms and Carbon Monoxide Alarms.
New Sections and Text: R313.3 Carbon Monoxide Alarms. At least one carbon monoxide alarm shall be installed in the immediate vicinity of the bedroom(s) on the lowest floor level of the dwelling unit containing bedroom(s).
All carbon monoxide alarms shall be listed and installed in accordance with the provisions of this code and the provisions of NFPA 720.
R313.4 Power Source. Carbon monoxide alarms are permitted to be permanently connected to the building wiring when such wiring is served from a commercial source or shall receive power from one or more batteries.
Where a battery is employed as a main supply, its depletion below the level at which an alarm signal would be obtained shall be indicated by a distinctive audible trouble signal that persists for at least seven days.
Carbon monoxide alarms are not to be used as a substitute or in lieu of the smoke alarms required in this section.
Fiscal Impact Statement [Provide documentation of the costs and benefits of the proposed modifications to the code for each of the following entities. Cost data should be accompanied by a list of assumptions and supporting documentation. Explain expected benefits.]:
A. Impact to local entity relative to enforcement of code: Minimal. The code already requires the installation of similar devices such as smoke alarms. No additional training would be required or time allotted for inspections of CO devices.
B. Impact to building and property owners relative to cost of compliance with code: CO alarms cost in a range of $25 for the most basic units to as high as $55 for combination type and digital devices.
C. Impact to industry relative to cost of compliance with code: The state of Florida construction industry currently builds an average of 165,000 homes per year. At an average cost of $40 dollars per home for CO alarms, the fiscal impact could be as high as 6.5 million dollars per year.
Rationale [Provide an explanation of why you would like this Proposed Modification to the Florida Building Code.]:
Carbon Monoxide is an odorless, colorless, tasteless, and highly poisonous gas that can cause ill-effects at concentrations of only 50 ppm. The Journal of American Medical Association estimates approximately 1,600 deaths each year to CO poisoning in the US. The Consumer Product Safety Commission reports that 200-300 persons die each year to equipment/ventilation malfunction of fuel burning household appliances. Over 10,000 are diagnosed each year with CO-related injuries. Based on this information, it appears many more people die each year from CO poisoning than those that do from electrocution.
In Florida alone, the use of portable generators resulted in the death of 18 persons in 2001, 40 in 2002, and 36 in 2003. 6 persons died in the state of Florida following the 2004 hurricane season from CO poisoning, 4 following the 2005 hurricane season. 167 persons were hospitalized in Florida following the 2004 hurricane season
More than 50% of CO deaths are persons of 65 and older. The major symptoms of CO poisoning are commonly misdiagnosed in the elderly. Florida has the largest number of 65 and older persons in the US.
Since the year 2000, sales of portable generators have been increasing. In 2004 alone, 380,000 units were sold in the US to households. The cost of portable generators has been steadily decreasing over this same period.
Per the Centers for Disease Control and Prevention, the exhaust produced by the typical 5.5 kW generator contains as much CO as six idling automobiles.
96% (160) of all non-fatal and 5 of the fatal incidents of CO poisoning following the 2004 hurricane season were directly related to gasoline-powered generators. The CDC reports that 17.5% of Florida households used a portable generator after at least one of the 2004 hurricanes. Medical records from patients indicated that generators were installed in garages, in porches, and within the home to protect the units from weather or from being stolen. Other locations included near open windows and near room air conditioners (window-mounted units).
Hurricanes seasons since 2000 are lasting longer and producing more intense and more land falling storms. In 2002 there were 14 named storms and 4 hurricanes, in 2003 there were 21 named storms and 7 hurricanes, in 2004 there were 16 named storms and 9 hurricanes ? 6 storms directly effecting Florida, in 2005 there were 27 named storms, 15 hurricanes, seven major hurricanes of Category 3 or higher with 6 having a US landfall.
Please explain how the proposed modification meets the following requirements:
1. Has a reasonable and substantial connection with the health, safety, and welfare of the general public: Yes, see the above substantiation.
2. Strengthens or improves the code, and provides equivalent or better products, methods, or systems of construction: Yes, adds a needed safeguard for public safety.
3. Does not discriminate against materials, products, methods, or systems of construction of demonstrated capabilities: Yes
4. Does not degrade the effectiveness of the code: Yes, meets the purpose of the code as stated in Section R101.3 of the Florida Residential Code.