Welcome back from me as well. Yeah, 140+A for 4 minutes is a big deal on a 60A breaker when it's smoking. Could you link the UL standard you found for those breakers? The one I found:
http://static.schneider-electric.us...100-400 A Frame FA-LA/FA-FC-FH/0600DB0105.pdf
shows that a breaker should trip within 100 seconds if it sees ~1.4-2x its rated current. For a 60A, that's 84-120A in a minute forty seconds. At nearly 2.5x its rated capacity, trip time should be ~15-55 seconds.
Trip curves of manufactures will always be less than the UL Standard. A copy of the UL Standard in question is something like $2700. What I posted is a general rule of thumb that was mentioned at an electrical seminar by a UL narrator a couple of years ago.
Today’s breakers open under thermal, magnetic, and electronic sensors. The old FPE breakers only opened under thermal only therefore the bad publicity.
With today’s technology it is easy to trash something we know nothing about. If you take the time to do research on FPE and Zinsco you will find that most to the bad stuff reported is done so by Home Inspectors and a lot of the information is false. Watching some video of someone welding with a breaker is far from any type of testing. Testing is done by a third party in a testing lab and anything seen on the internet is nothing more than entertainment.
The main problem with these breakers were they opened only after getting hot, very hot if they were the larger size or of more than one pole. This heat caused problems with not only the internal parts of the breaker but also the bus bars.
Now to just sit and trash something just because someone else did I think that Dale should run his last race in Homeland with a 1906 Ford then we would have a good comparison to the old breakers and today’s product. :lol: