Federal Pioneer 400amp switch

Status
Not open for further replies.

powerplay

Senior Member
Location
Canada
Occupation
Electrical Contractor
I was told that I could put in a 200amp fuse into a 400 amp FPE Disconnect Switch... i put one in, but it was loose! Is there an adapter?...or not rated for the smaller fuse??
 
Depending if your conductors being protected are large enough you could use 225 amp fuses and not need adapters.
 