ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Consulting Electrical Engineer - Photovoltaic Systems
A design I am reviewing has a PV interconnection through a 70A breaker in a 225A (bus rating) MDP with a 200A main breaker. The designer has the PV breaker at the opposite end of the bus from the main, so it would be OK by the 120% rule except that the MDP is a feedthrough design with a 200A panel with a 200A main on the feed through lugs. I am inclined to direct him to move the subpanel to a 200A load breaker in the MDP. What say you?