Feed to garage

Status
Not open for further replies.

guschash

Senior Member
Location
Ohio
I had a question put to me today that I didn't know how to answer. They ask me if they could have one 20 amp circuit going to the garage. I said sure and they said overhead and what type of wire. Where do I find the answer in the code book? 230.202 SEC (A) mentons conductor size but this one circuit not a service. I have to leave now so I'll check back later.

Thanks
Gus
 
I had a question put to me today that I didn't know how to answer. They ask me if they could have one 20 amp circuit going to the garage. I said sure and they said overhead and what type of wire. Where do I find the answer in the code book? 230.202 SEC (A) mentons conductor size but this one circuit not a service. I have to leave now so I'll check back later.

Thanks
Gus

230.202? 230 is for services, not branch circuits. And 230.202 is for services over 600V.
 
I had a question put to me today that I didn't know how to answer. They ask me if they could have one 20 amp circuit going to the garage. I said sure and they said overhead and what type of wire. Where do I find the answer in the code book? 230.202 SEC (A) mentons conductor size but this one circuit not a service. I have to leave now so I'll check back later.

Thanks
Gus

Art. 225 part II will get you started and Uf may be used with a messenger support 340.12(11)
 
Thanks for the replies. Read 340.12 and 396 and 225.4 and 225.6. I think 225.4 and 225.6 was what I was looking for. Thanks



gus
 