Is it NEC code compliant to feed a 50 amp subpanel with a four wire # 6 Aluminum SER cable, using the 75 C column of Table 310.16, since the wire is rated at 90 C and breaker and subpanel are rated at 75 C.
I determined this from NEC 110.14 (C)(1)(a)(3) and NEC 338.10(B)(4)(a)(1) and (3).
Thank you.
I determined this from NEC 110.14 (C)(1)(a)(3) and NEC 338.10(B)(4)(a)(1) and (3).
Thank you.