I am upgrading a small portion of a feeder system. I am using 25' tap rule for 3 Loads off of a 1600Amp Breaker. I sized parallel 350 to protect to one third of the 1600A.
Tap one feeds a 400 Amp Disconnect to protect a previously installed 500 running to a distribution panel with a 600 Amp Main Breaker.
Tap Two feeds an auxiliary switchgear with 2 loads 1. 350hp motor 2. 150hp motor. Both Motors are non-Continuous
Tap Three feeds a distribution panel with a 600 Amp Main Breaker.
For the Main Feeder breaker for this circuit 1600A Sensor:
I am looking for help on why the LTPU cannot be set above 620 Amps?
I want to ensure that there are no errand trips on the 1600 Amp Breaker.
Thank you for your help!
Brian