I understand National Electric Code. Section 210.20(A) which basically says that a circuit breaker for a branch circuit must be rated such that it can handle the noncontinuous load plus 125% of the continuous load. (A continuous load is one where the maximum current is expected to continue for 3 hours or more.) In other words, the breaker needs an extra 25% capacity of the continuous load for headroom.
How does this apply to the breaker in the distribution panel feeding the panelboard with all the branch circuits?
I always assumed that breaker to just be sized based on total load in the panel plus 125% so taking the connected load of all the branch circuits in the panel and adding 125% to come up with the breaker size to feed the panel.
For example, a 100A panelboard fed with a 100A breaker in a distribution panel should not have more than 80A of connected load.
Is this a NEC requirement for sizing this part of the distribution system or just good engineering practice.
Thanks for your response.
How does this apply to the breaker in the distribution panel feeding the panelboard with all the branch circuits?
I always assumed that breaker to just be sized based on total load in the panel plus 125% so taking the connected load of all the branch circuits in the panel and adding 125% to come up with the breaker size to feed the panel.
For example, a 100A panelboard fed with a 100A breaker in a distribution panel should not have more than 80A of connected load.
Is this a NEC requirement for sizing this part of the distribution system or just good engineering practice.
Thanks for your response.