romex jockey
Senior Member
- Location
- Vermont
- Occupation
- electrician
500kcmil has been a standard for a 400A service for how long?
~RJ~
~RJ~
Only where the calculated load is 380 amps or less. It has never been permitted for a load higher than its ampacity of 380 amps.500kcmil has been a standard for a 400A service for how long?
~RJ~
Oh I gotcha.Actually it is not about the index, if you look at the pages past the index you will find instructions of how to make a proposal or PI.
Roger
Well for residential 1 fam, it's 400 MCM.Only where the calculated load is 380 amps or less. It has never been permitted for a load higher than its ampacity of 380 amps.
Somehow, we are making a mountain out of a mole hill. According to your post, you are doing plans review and you show a 390 amp load on a 500 kcmil conductor.I have feeder breaker 400A that has feeder cable 500kcmil CU feeding 400A MLO panel A.
Panel A demand load comes out to 390A both continuous and non continuous load.
Would the feeder cable size of 500kcmil ok or does it need to be upsized?
Assume 75C
You would still have the 110.14 limitations to the 75deg ratingI wonder, since it's a feeder (probably inside)
What's the ambient temperature?
380 amps is at 86 degrees farenheit.
If your ambient temperature is lower than 86 degrees, your 500 kcmil is good for 410 amps
I'm not sure what you think you see there that would affect the ampacity of a conductor relative to ambient temperatureYou would still have the 110.14 limitations to the 75deg rating
so somehow a demand load calc is part of this code loop?Only where the calculated load is 380 amps or less. It has never been permitted for a load higher than its ampacity of 380 amps.
Doesn't affect the ampacity of the conductor, but he's still limited to terminate at the 75 deg ampacity due to the 110.14 limits.I'm not sure what you think you see there that would affect the ampacity of a conductor relative to ambient temperature
75 degrees is not an ampacity, it's a temperature.Doesn't affect the ampacity of the conductor, but he's still limited to terminate at the 75 deg ampacity due to the 110.14 limits.
If the ambient temperature is lower than 78 degrees fahrenheit, then 399 amps would be under 75 degrees Celsius.(C) Temperature Limitations. The temperature rating associ ated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor, or device. Conductors with temperature ratings higher than specified for termi nations shall be permitted to be used for ampacity adjustment, correction, or both.
In 35 years I have never seen an installation where you could use an ambient temperature below 30° C so for me it's not something that will ever have a real world use. Regarding the OP the same thing is probably true.If the ambient temperature is lower than 78 degrees fahrenheit, then 399 amps would be under 75 degrees Celsius.
Like I said, temperature and amperage aren't the same thing.
If the ambient temperature was 50 degrees Fahrenheit, that 500kcmil conductor and all the terminals would be good for 475 amps, and would not exceed 75 degrees Celsius
Both, because ambient temperature directly affects the operating temperature of conductors and connections.So one has to look out for number of current carrying conductors in conduit adjustment, ambient temperatures adjustment too?
well I am confused. Does ambient temperature apply to conductors cables only or to the terminations temperature or both?
Why is that? Are you suggesting you've never installed wiring in an atmosphere where temperature is controlled to always be below 86 degrees farenheit?In 35 years I have never seen an installation where you could use an ambient temperature below 30° C so for me it's not something that will ever have a real world use.
That would seem to make sense from physics.Both, because ambient temperature directly affects the operating temperature of conductors and connections.
Yes, but how many amps is a termination rated for? As far as I know, they aren't. They're rated for temperature. It's possible they are rated for amperage. In that case, a larger lug would suffice.That would seem to make sense from physics.
But 110.14(C) is generally understood not to allow or require temperature correction at terminations. I believe the citation is the (2017) portion of 110.14(C)(1) that says ". . . conductor ampacities used in determining equipment termination provisions shall be based on Table 310.15(B)(16) as appropriately modified by 310.15(B)(7)." Since that section references the tables directly, without referencing ampacity correction or adjustment, those do not apply for equipment terminations.
Cheers, Wayne
That is an interesting question. I think it has been suggested that an equipment termination rated at 75C accepting a maximum wire size of, say, #3 Cu must be rated for 100A. Not sure about that.Yes, but how many amps is a termination rated for? As far as I know, they aren't.