Not really for panelboard breaker protection 408.30 and 408.36 says section see 220. If you do the continous plus non continuous then it maybe come out greater than 220 method but then 408.30 and 408.36 say you cannot do this thus reason for asking the question.
Here we go, what looks like more disjointed codes. 215.2 says to size conductors plus maybe any increases for continuous loads using 220.
215.3 says size protection for feeder by criteria in 240 part I.
240.3 indicated certain equipment to be protected by respective relevant section list in table 240.3, 408 is one, and supersede aspects of 240.
408.30 mearly says that it is sized for
minimum feeder capacity required for a load calculated
in accordance with parts III,IV,V of Article 220.
The feeder capacity when sized properly to Article 215 will be sized
in accordance with those 220 parts. And if panel is sized appropriately will meet the amperage related to the feeder capacity.
215.3 also includes exception for use of a 100% breaker and equipment eliminating the 125% increase for continuous loads. If panelboard is listed to be rated to 100% of load capacity along with protective breaker it meets the requirements of 215.3 Exception 1. would allow a simple sum of loads without the 125% increase for the breaker, and panel capacity.
408.36 says you can't have a panelboard rated less that the protective protective device, so you cant have a panelboard that is rated for ie. 200Amp protected by a 250Amp breaker. So if you back this information out would simply indicate 2 options for the panelboard. 1. Get a bigger panelboard. or 2. Reduce the loads on the panelboard.