I think you have the concept backwards. The "load" isn't derated, the ampacity of the conductor is derated.Wayne I think you answered my question here, albeit inadvertently. So even though my conductor at 60 degrees is rated at 20 amps, it still remains a viable option since its ampacity can suffice the maximum total load of my feeders. There's been a lot of talk around the shop, that the ampacities under the 60 degree column need to support, not the maximum total load of my feeders, but the derated load of my feeders (23.8 amps).
You need a conductor that has an ampacity of at least 16.56A after the application of any adjustment or correction factors.