Understood ggunn. Yes I knew that, hence the upgrading of both sub-panels B1 and B2 to 200A rated, and downsizing the main from 400A to 350A.
My concern is 100A of solar OCPD exporting through #4 THHN. Existing feeders from B1 to B2 are #4 THHN and are protected by 100A breaker. B2 is in a guest house. Inverter max output currents are 47.5A and 32A, two inverters. What are your thoughts? 100A of solar OCPD exporting through #4 THHN okay?