cadpoint
Senior Member
- Location
- Durham, NC
I would say that no OC device is needed as well as no EGC is needed run to the building. These are service conductors, and not a feeder. Unless the building falls under 547 then an EGC will be needed, if direct buried must be insulated or covered copper, but overcurrent protection at the pole is still not needed.
I hope you said all that correct. I didn't check anything, but I heartly agree.
My first thought - hmm, 6000 Sq Ft - Shed = Agricultural Buildings, Article 547.
I'd suggest a complete review of the article, and maybe a chat with AHJ about shed size limits. You have to watch out for farmers, nice people but also very cleaver.