I've never properly understood all of Article 430 Part V. So maybe someone could help me understand the following example:
A feeder supplies a non-continuous, non-motor load of 40A along with 2 motors with a Table FLC of 40A each. No derating is required and all terminations are 75C. What is the minimum allowable Cu 90C insulated conductor size, and what is the allowable range of standard size inverse time breaker(s) that may be used for those conductors?
Note I haven't specified voltage or number of phases. I don't think those matter, but if I'm mistaken and they do, let's say 240V, single phase (so the motors are 7.5 HP per FLC in Table 430.248).
Thanks, Wayne
A feeder supplies a non-continuous, non-motor load of 40A along with 2 motors with a Table FLC of 40A each. No derating is required and all terminations are 75C. What is the minimum allowable Cu 90C insulated conductor size, and what is the allowable range of standard size inverse time breaker(s) that may be used for those conductors?