I'm trying to calculate the size of a wire I would need for a feeder. I need to run about 2500 ft at 277 480 volts to a step down 120 208 transformer and get 200 amps on the secondary

I'm having a brain fart on how to calculate the size of the primaries

Sent from my SM-S906U using Tapatalk
 

nickelec

Senior Member
Location
US
Does it pay to use the step up transformer and then another step down at the end

Sent from my SM-S906U using Tapatalk
 

nickelec

Senior Member
Location
US
Could that even be done 480 stepped up to MV. I've never done that before..

Just trying to help a customer out with some viable options

Sent from my SM-S906U using Tapatalk
 
Could that even be done 480 stepped up to MV. I've never done that before..
Not uncommon and for half a mile, might well be worth it, but you have to do the pricing exercise to know. Also depends on whether you can/are allowed to run MV around, could be a local restriction or no good place to put the cables.

Is this going in pipe or overhead? Much easier to do MV if it's overhead.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
"Shore Power" = Marina or Dock
55.4 in the '17 prohibits over 1000 volt
 