I'm trying to calculate the size of a wire I would need for a feeder. I need to run about 2500 ft at 277 480 volts to a step down 120 208 transformer and get 200 amps on the secondary

I'm having a brain fart on how to calculate the size of the primaries

Sent from my SM-S906U using Tapatalk
 
Does it pay to use the step up transformer and then another step down at the end

Sent from my SM-S906U using Tapatalk
 
Could that even be done 480 stepped up to MV. I've never done that before..

Just trying to help a customer out with some viable options

Sent from my SM-S906U using Tapatalk
 
Could that even be done 480 stepped up to MV. I've never done that before..
Not uncommon and for half a mile, might well be worth it, but you have to do the pricing exercise to know. Also depends on whether you can/are allowed to run MV around, could be a local restriction or no good place to put the cables.

Is this going in pipe or overhead? Much easier to do MV if it's overhead.
 
"Shore Power" = Marina or Dock
55.4 in the '17 prohibits over 1000 volt
 